Nitrogen leak testing
I got a nitrogen regulator and bottle for checking leaks. What pressure should I use? How long to let the system rest with no drop in pressure to call it good?
Re: Nitrogen leak testing
I've been told several times and read a few places to go to 150 psi. That is what psi I use. I usually let mine rest 30-60 minutes but I know some people let it sit overnight.
Re: Nitrogen leak testing
That is what I understood as well. Something I read a long time ago, evap cores are designed for burst pressure of 150psi.
------------------------------
Please support ACKITS.com for your Auto A/C Parts and Tool needs.
Help Support the Forum
Please support ACKITS.com for your Auto A/C Parts and Tool needs.
Help Support the Forum
Re: Nitrogen leak testing
I pressurized the system and sprayed down the lines to check for leaks. Found the upper condenser fitting leaking,
I replaced the o-ring and pressurized it again to 175 psi at 7:30 pm yesterday with 76°F. Do I still have a leak or are these readings normal?
9:30 pm 72° 145 psi
11:00 pm 71° 145 psi
7:30 am 67° 140 psi
I can assume the overnight drop of 5 psi is from the drop in temperature. What about the 30 psi drop in the first 2 hours? Is that just the nitrogen migrating throughout the system?
I replaced the o-ring and pressurized it again to 175 psi at 7:30 pm yesterday with 76°F. Do I still have a leak or are these readings normal?
9:30 pm 72° 145 psi
11:00 pm 71° 145 psi
7:30 am 67° 140 psi
I can assume the overnight drop of 5 psi is from the drop in temperature. What about the 30 psi drop in the first 2 hours? Is that just the nitrogen migrating throughout the system?
Re: Nitrogen leak testing
Re: Nitrogen leak testing
I would think that you shouldn't have any significant drop if you don't have a leak but since it didn't drop much for about 10 hours, I don't know. The temperature drop is not that much during the 12 hours time period so I wouldn't think it would cause the 35 degree total drop.atikovi wrote: ↑Thu Aug 03, 2023 6:02 am I pressurized the system and sprayed down the lines to check for leaks. Found the upper condenser fitting leaking,
I replaced the o-ring and pressurized it again to 175 psi at 7:30 pm yesterday with 76°F. Do I still have a leak or are these readings normal?
9:30 pm 72° 145 psi
11:00 pm 71° 145 psi
7:30 am 67° 140 psi
I can assume the overnight drop of 5 psi is from the drop in temperature. What about the 30 psi drop in the first 2 hours? Is that just the nitrogen migrating throughout the system?
Re: Nitrogen leak testing
Well, at 10 am it was still at 140 so I vacuumed 2 hours and then charged. Will see how long it lasts.
Re: Nitrogen leak testing
A 5 psi drop at rest wouldn't be a way to measure if you lost some refrigerant. I would attribute that to a temperature change.
The soapy water test is a better way to test than with dye. I prefer an electronic leak detector but would be fine with soapy water in lieu of.
Nice job diagnosing.
The soapy water test is a better way to test than with dye. I prefer an electronic leak detector but would be fine with soapy water in lieu of.
Nice job diagnosing.
Re: Nitrogen leak testing
Here's a nitrogen pressure calculator. I have found that it follows what Fieldpiece uses for their temperature compensation in their gauges for their "tightness test."
https://www.oceanhvac.com/nitro.php
https://www.oceanhvac.com/nitro.php