Nitrogen leak testing

Post by atikovi »

I got a nitrogen regulator and bottle for checking leaks. What pressure should I use? How long to let the system rest with no drop in pressure to call it good?

Image
70monte
Posts: 54
Joined: Fri May 13, 2016 9:03 pm

Re: Nitrogen leak testing

Post by 70monte »

I've been told several times and read a few places to go to 150 psi. That is what psi I use. I usually let mine rest 30-60 minutes but I know some people let it sit overnight.
User avatar
Tim
Site Admin
Posts: 1279
Joined: Tue Apr 12, 2016 2:19 pm
Location: Scottsdale, Arizona
Contact:

Re: Nitrogen leak testing

Post by Tim »

70monte wrote: Wed Aug 02, 2023 4:48 pm I've been told several times and read a few places to go to 150 psi. That is what psi I use. I usually let mine rest 30-60 minutes but I know some people let it sit overnight.
That is what I understood as well. Something I read a long time ago, evap cores are designed for burst pressure of 150psi.
------------------------------
Please support ACKITS.com for your Auto A/C Parts and Tool needs.

Help Support the Forum
atikovi
Posts: 119
Joined: Wed Jul 06, 2016 3:01 pm
Location: Suburban Washington DC

Re: Nitrogen leak testing

Post by atikovi »

I pressurized the system and sprayed down the lines to check for leaks. Found the upper condenser fitting leaking,

Image

I replaced the o-ring and pressurized it again to 175 psi at 7:30 pm yesterday with 76°F. Do I still have a leak or are these readings normal?

9:30 pm 72° 145 psi
11:00 pm 71° 145 psi
7:30 am 67° 140 psi

I can assume the overnight drop of 5 psi is from the drop in temperature. What about the 30 psi drop in the first 2 hours? Is that just the nitrogen migrating throughout the system?
70monte
Posts: 54
Joined: Fri May 13, 2016 9:03 pm

Re: Nitrogen leak testing

Post by 70monte »

Tim wrote: Wed Aug 02, 2023 5:29 pm
70monte wrote: Wed Aug 02, 2023 4:48 pm I've been told several times and read a few places to go to 150 psi. That is what psi I use. I usually let mine rest 30-60 minutes but I know some people let it sit overnight.
That is what I understood as well. Something I read a long time ago, evap cores are designed for burst pressure of 150psi.
Yes, the evap seems to be the weak link as far as pressures go for testing purposes. 150 psi seems to work fine.
70monte
Posts: 54
Joined: Fri May 13, 2016 9:03 pm

Re: Nitrogen leak testing

Post by 70monte »

atikovi wrote: Thu Aug 03, 2023 6:02 am I pressurized the system and sprayed down the lines to check for leaks. Found the upper condenser fitting leaking,

Image

I replaced the o-ring and pressurized it again to 175 psi at 7:30 pm yesterday with 76°F. Do I still have a leak or are these readings normal?

9:30 pm 72° 145 psi
11:00 pm 71° 145 psi
7:30 am 67° 140 psi

I can assume the overnight drop of 5 psi is from the drop in temperature. What about the 30 psi drop in the first 2 hours? Is that just the nitrogen migrating throughout the system?
I would think that you shouldn't have any significant drop if you don't have a leak but since it didn't drop much for about 10 hours, I don't know. The temperature drop is not that much during the 12 hours time period so I wouldn't think it would cause the 35 degree total drop.
atikovi
Posts: 119
Joined: Wed Jul 06, 2016 3:01 pm
Location: Suburban Washington DC

Re: Nitrogen leak testing

Post by atikovi »

Well, at 10 am it was still at 140 so I vacuumed 2 hours and then charged. Will see how long it lasts.
User avatar
Cusser
Preferred Member
Posts: 949
Joined: Sun Apr 24, 2016 6:29 am

Re: Nitrogen leak testing

Post by Cusser »

atikovi wrote: Thu Aug 03, 2023 11:08 am Well, at 10 am it was still at 140 so I vacuumed 2 hours and then charged. Will see how long it lasts.
I think you made the logical choice.

For that area, you can test for leaks with soap bubbles.
tony1963
Posts: 68
Joined: Fri Nov 27, 2020 11:37 am

Re: Nitrogen leak testing

Post by tony1963 »

A 5 psi drop at rest wouldn't be a way to measure if you lost some refrigerant. I would attribute that to a temperature change.

The soapy water test is a better way to test than with dye. I prefer an electronic leak detector but would be fine with soapy water in lieu of.

Nice job diagnosing.
User avatar
Q451990
Posts: 10
Joined: Mon Jul 31, 2023 9:10 pm

Re: Nitrogen leak testing

Post by Q451990 »

Here's a nitrogen pressure calculator. I have found that it follows what Fieldpiece uses for their temperature compensation in their gauges for their "tightness test."

https://www.oceanhvac.com/nitro.php