jtupper wrote: Sun May 22, 2022 12:08 pm
The manifold gauges were a loaner set as well. I took the pump back to AutoZone and got a different one from Oreilly's. Same result. I started looking at the o-rings in the hoses and they were pretty gnarly. I ended up picking up a brand new set of gauges. Full disclosure, they are the Harbor Freight set. I hooked up the pump to the new gauges and it vacuumed down to 26 Hg within a minute or so. It wont vacuum down below 26 Hg, but it has only been a few minutes.
Well, 26 InHg is better than last time but still inadequate. Since you have a new Manifold Gauge Set connected, that would seem to rule out leakage at the knurled hose ends and the MGS itself. It must still be a weak vacuum pump since the system itself maintains the maximum pump vacuum over time. Try running the VP for about one hour and see whether the vacuum reading drops. If not, I would suspect either the oil again or an abused VP that just will no longer pull an acceptable vacuum.
jtupper wrote: Sun May 22, 2022 12:08 pm
Can I assume there are no leaks in the system since it held vacuum overnight? The vacuum actually increased overnight to
20 Hg. I don't understand that (ambient temp?). I'm going to let the pump run for a while to see if it will vacuum down any lower. I'm kind of at a loss here. BTW...I'm in Houston so I'm at or just above sea level.
Typo? I think you must have meant 28 InHg and not 20 InHg. I can't explain why the reading would increase slightly overnight.
Sometimes, a system can hold vacuum indefinitely but leak under pressure, and vice-versa. So because it held vacuum overnight is no assurance that it won't leak after charging.
Since you're virtually at sea level, you should see a vacuum of 29.9 InHg or better. But you would need a micron gauge to measure a lower vacuum reading (in microns) because at that reading, you'll be at the practical lower limit of your low-side gauge. For your purposes, 29.9 InHg should suffice, though.