Determining correct charge weight for non-stock A/C
Posted: Sun Jul 24, 2016 9:39 pm
Trying to find out how to determine correct charge level for a non-stock system. Have a V5 compressor on a chevy 4.8 LS motor in a '94 C1500 pickup. Original evaporator, new accumulator, aftermarket parallel flow condenser, stock black/white orfice tube, dual electric fans, custom hoses within a few inches of the old R4 setup.
Stock capacity of the R4 system was 32oz, charged to that and it cooled "ok" center vent ~48deg on a 80deg day. Couldn't id the RCV that was on the compressor but was destroking ~44psi. Switched out to a green valve (37psi), much colder but froze up the evap. Switched out to a purple 41psi valve
Last few days have been 90+ and <50% RH. Center vent 43-44deg going down the road but warms up into the high 50's in stop n go traffic. Recirc door is closing. With 32oz charge at idle was seeing 40/175, wetting down condenser dropped to 160psi and little change in vent temp.
Adding 4oz R134 made no difference, 2oz more still no difference. Recovered and recharged with 16oz, started up system and slowly added watching vent temps and pressure. At 22oz in recirc mode with high fan have 25/180psi, vent temp 46 at idle. With fan on low 41/150, vent 43. Vent temp 43-44 going down the road in 90deg ambient. Can now hear the compressor working harder at idle. Thinking it was overcharged at 32oz, possibly flooding the condenser?
I read here and other forums that (especially) variable disp systems need to be charged to the correct weight but how did the factory determine that? Superheat? Condenser delta-T? "Hey Louie, this is cold enough how much did you put in?"
Stock capacity of the R4 system was 32oz, charged to that and it cooled "ok" center vent ~48deg on a 80deg day. Couldn't id the RCV that was on the compressor but was destroking ~44psi. Switched out to a green valve (37psi), much colder but froze up the evap. Switched out to a purple 41psi valve
Last few days have been 90+ and <50% RH. Center vent 43-44deg going down the road but warms up into the high 50's in stop n go traffic. Recirc door is closing. With 32oz charge at idle was seeing 40/175, wetting down condenser dropped to 160psi and little change in vent temp.
Adding 4oz R134 made no difference, 2oz more still no difference. Recovered and recharged with 16oz, started up system and slowly added watching vent temps and pressure. At 22oz in recirc mode with high fan have 25/180psi, vent temp 46 at idle. With fan on low 41/150, vent 43. Vent temp 43-44 going down the road in 90deg ambient. Can now hear the compressor working harder at idle. Thinking it was overcharged at 32oz, possibly flooding the condenser?
I read here and other forums that (especially) variable disp systems need to be charged to the correct weight but how did the factory determine that? Superheat? Condenser delta-T? "Hey Louie, this is cold enough how much did you put in?"