Water Dripping from Evap, suction line warm
Posted: Sat May 20, 2017 6:01 am
So here's a mind twister.....been working on a piece of heavy equipment with a very odd situation. System when running will drip water from evaporator and will have air out vents at mid to high 40's if it stays between 60 and 70 degrees outside suction line never cold and high side lines at drier never hot to the touch. When it warms up at outside air out vents goes up to mid 50's to 60's still see water drip from evap, suction line not cold. This is on a expansion valve system. Compressor cycles every 6 or 8 seconds down to 6lbs then I assume the low pressure switch is shutting it off, high side is 125- 150 depending on outside temp and independent condenser fan is running normal so no issues there. I suggested to customer evaporator is likely covered with dirt and mud as most construction stuff gets and while we had it apart should replace expansion valve as I think it's starving for Freon. At first it appeared as a low charge but system was just recharged by someone else and tagged as full charge. Customer decided to ignore my advice and change binary switch my thinking was since the switch is shutting the system off it's functioning normally.....thoughts ????