Nitrogen leak testing
Posted: Wed Aug 02, 2023 12:18 pm
by atikovi
I got a nitrogen regulator and bottle for checking leaks. What pressure should I use? How long to let the system rest with no drop in pressure to call it good?
Re: Nitrogen leak testing
Posted: Wed Aug 02, 2023 4:48 pm
by 70monte
I've been told several times and read a few places to go to 150 psi. That is what psi I use. I usually let mine rest 30-60 minutes but I know some people let it sit overnight.
Re: Nitrogen leak testing
Posted: Wed Aug 02, 2023 5:29 pm
by Tim
70monte wrote: ↑Wed Aug 02, 2023 4:48 pm
I've been told several times and read a few places to go to 150 psi. That is what psi I use. I usually let mine rest 30-60 minutes but I know some people let it sit overnight.
That is what I understood as well. Something I read a long time ago, evap cores are designed for burst pressure of 150psi.
Re: Nitrogen leak testing
Posted: Thu Aug 03, 2023 6:02 am
by atikovi
I pressurized the system and sprayed down the lines to check for leaks. Found the upper condenser fitting leaking,
I replaced the o-ring and pressurized it again to 175 psi at 7:30 pm yesterday with 76°F. Do I still have a leak or are these readings normal?
9:30 pm 72° 145 psi
11:00 pm 71° 145 psi
7:30 am 67° 140 psi
I can assume the overnight drop of 5 psi is from the drop in temperature. What about the 30 psi drop in the first 2 hours? Is that just the nitrogen migrating throughout the system?
Re: Nitrogen leak testing
Posted: Thu Aug 03, 2023 9:22 am
by 70monte
Tim wrote: ↑Wed Aug 02, 2023 5:29 pm
70monte wrote: ↑Wed Aug 02, 2023 4:48 pm
I've been told several times and read a few places to go to 150 psi. That is what psi I use. I usually let mine rest 30-60 minutes but I know some people let it sit overnight.
That is what I understood as well. Something I read a long time ago, evap cores are designed for burst pressure of 150psi.
Yes, the evap seems to be the weak link as far as pressures go for testing purposes. 150 psi seems to work fine.
Re: Nitrogen leak testing
Posted: Thu Aug 03, 2023 9:27 am
by 70monte
atikovi wrote: ↑Thu Aug 03, 2023 6:02 am
I pressurized the system and sprayed down the lines to check for leaks. Found the upper condenser fitting leaking,
I replaced the o-ring and pressurized it again to 175 psi at 7:30 pm yesterday with 76°F. Do I still have a leak or are these readings normal?
9:30 pm 72° 145 psi
11:00 pm 71° 145 psi
7:30 am 67° 140 psi
I can assume the overnight drop of 5 psi is from the drop in temperature. What about the 30 psi drop in the first 2 hours? Is that just the nitrogen migrating throughout the system?
I would think that you shouldn't have any significant drop if you don't have a leak but since it didn't drop much for about 10 hours, I don't know. The temperature drop is not that much during the 12 hours time period so I wouldn't think it would cause the 35 degree total drop.
Re: Nitrogen leak testing
Posted: Thu Aug 03, 2023 11:08 am
by atikovi
Well, at 10 am it was still at 140 so I vacuumed 2 hours and then charged. Will see how long it lasts.
Re: Nitrogen leak testing
Posted: Fri Aug 04, 2023 7:55 am
by Cusser
atikovi wrote: ↑Thu Aug 03, 2023 11:08 am
Well, at 10 am it was still at 140 so I vacuumed 2 hours and then charged. Will see how long it lasts.
I think you made the logical choice.
For that area, you can test for leaks with soap bubbles.
Re: Nitrogen leak testing
Posted: Sun Aug 06, 2023 11:56 am
by tony1963
A 5 psi drop at rest wouldn't be a way to measure if you lost some refrigerant. I would attribute that to a temperature change.
The soapy water test is a better way to test than with dye. I prefer an electronic leak detector but would be fine with soapy water in lieu of.
Nice job diagnosing.
Re: Nitrogen leak testing
Posted: Sun Aug 06, 2023 6:18 pm
by Q451990
Here's a nitrogen pressure calculator. I have found that it follows what Fieldpiece uses for their temperature compensation in their gauges for their "tightness test."