Posted: Thu Feb 02, 2023 2:31 am
Good evening all,
I hope noone takes objection to me posting on here about an earthmoving machine...
Long time lurker on the forums here, finally registered an account hopefully to have someone point out something I have missed on this machine.
I am an auto electrician with 10+ years experience, VASA member and RTA account holder down under and have a Hyundai Excavator thats causing me to tear my hair out at the moment.
The machine is a R145-CR9, I originally did a service call to the machine in December and found that the Compressor was just begining to sieze, it didnt lock up had tight spots when rotating the Compressor by hand. Drained the oil and couldnt see any evidence of a internal failure no metal swarf etc. So I supplied and fitted a new Compressor, TXV, and drier. I flushed the lines and reverse flushed the heat exchangers, left them in the sun for better part of two days and ran high pressure nitrogen through them to ensure I had no flush left over all seemed ok.
I purged the air from the lines when everything was reassembled, changed over to tracer gas with hyrdogen and went all over no leaks detected. Applied big blue to all the unions etc all ok no indicated problems.
The Compressor is a Delphi v5, 24v single A section and has a Red Control valve (according to my book thats a 44psi set point.) I couldn't obtain the OE data for charge weight so I charged to a known spec I did on an indentical machine 12 months ago, 800g R134a, and monitored the pressures and subcooling as I weighed it in and everything seemed ok.
Admittedly it was not an ideal day to be doing the work as the day was a cool day and I was worried about the potential of overcharging it so I took a bunch of measurements on a performance sheet as follows, after running the machine for 20 mins. Sorry for you guys in the US for the metric measurements.
Ambient - 21c
RH - 77%
DP - 17c
Discharge Pressure - 850kpa
Converted to Temp - 38c
Condensor Inlet - 38c
Reciever Outlet - 28c
Suction Pressure - 200kpa
Water draining off - Yes
Vent Temp range - 5c-7c
Cycle time - Around 23 on 40 off.
Everything appeared OK and as normal. No complaints from the machine operator and I didnt hear back from them to say there was a problem.
Fast forward to last week.
Complaint was that it wasnt cooling after about half an hour of machine run time. I went out again, visually checked over the system nothing untoward apart from a loose drive belt. I grabbed the pulley and could turn the compressor by hand so it hadnt seized and had no tight spots. I tensioned the belt up and checked over, all appeared ok. I didnt take a performance test this time as I didnt believe there was anything wrong with it. I wound the engine speed up high to simulate the machine in work and no problems.
Chased up a replacement belt and fitted, run the machine for half hour, nipped the belt up again, tested, all working as far as I could tell.
Two days later I got a call to say that it had thrown a belt again. I attended, checked over the machine once again and couldnt see anything obviously wrong. Went to great effort to get a small ruler down in the guts of the machine to check if the pulley was somehow misaligned but it was spot on.
I grabbed the front of the compressor and once again can turn it freely by hand and no problem there. I removed the tensioner from the engine so I could sus out the condition of the idler bearing, no problems there, and no evidence of it being hot either.
Supplied and fitted another belt. Ran the machine at high speed, took another performance test. Readings as follows,
Ambient - 25c
RH - 95%
DP - 25c
Discharge Pressure - 1250kpa
Converted to Temp - 51c
Condensor Inlet - 52c
Reciever outlet - 38c
Suction Pressure - 200kpa
Water draining off - Yes
Vent Temp Range - 6-8c
Cycle time - Around 20 on 25 off.
I had a call today to tell me that the machine had run for about an hour today, before belt noises started and it eventually shredded another belt.
The only thing that doesn't quite resonate qith me is the suction pressure of 200kpa. I have never quite been able to get my head around the concept of the manual style control valve. If this compressor has a Red Delphi control valve with a setting of 44psi, that roughly comes to 300-ish kpa which I am significantly less than that and I have never seen a system cool properly at 300kpa.
Any opinions or feedback on anything that looks wrong from the other members here would be appreciated. I am out of ideas at the present moment. I really dont think that this is an alignment issue not considering it was fine for a month nearly two months before the problem began occuring.
I look forward to hearing from you all.
Regards,
OP.
I hope noone takes objection to me posting on here about an earthmoving machine...
Long time lurker on the forums here, finally registered an account hopefully to have someone point out something I have missed on this machine.
I am an auto electrician with 10+ years experience, VASA member and RTA account holder down under and have a Hyundai Excavator thats causing me to tear my hair out at the moment.
The machine is a R145-CR9, I originally did a service call to the machine in December and found that the Compressor was just begining to sieze, it didnt lock up had tight spots when rotating the Compressor by hand. Drained the oil and couldnt see any evidence of a internal failure no metal swarf etc. So I supplied and fitted a new Compressor, TXV, and drier. I flushed the lines and reverse flushed the heat exchangers, left them in the sun for better part of two days and ran high pressure nitrogen through them to ensure I had no flush left over all seemed ok.
I purged the air from the lines when everything was reassembled, changed over to tracer gas with hyrdogen and went all over no leaks detected. Applied big blue to all the unions etc all ok no indicated problems.
The Compressor is a Delphi v5, 24v single A section and has a Red Control valve (according to my book thats a 44psi set point.) I couldn't obtain the OE data for charge weight so I charged to a known spec I did on an indentical machine 12 months ago, 800g R134a, and monitored the pressures and subcooling as I weighed it in and everything seemed ok.
Admittedly it was not an ideal day to be doing the work as the day was a cool day and I was worried about the potential of overcharging it so I took a bunch of measurements on a performance sheet as follows, after running the machine for 20 mins. Sorry for you guys in the US for the metric measurements.
Ambient - 21c
RH - 77%
DP - 17c
Discharge Pressure - 850kpa
Converted to Temp - 38c
Condensor Inlet - 38c
Reciever Outlet - 28c
Suction Pressure - 200kpa
Water draining off - Yes
Vent Temp range - 5c-7c
Cycle time - Around 23 on 40 off.
Everything appeared OK and as normal. No complaints from the machine operator and I didnt hear back from them to say there was a problem.
Fast forward to last week.
Complaint was that it wasnt cooling after about half an hour of machine run time. I went out again, visually checked over the system nothing untoward apart from a loose drive belt. I grabbed the pulley and could turn the compressor by hand so it hadnt seized and had no tight spots. I tensioned the belt up and checked over, all appeared ok. I didnt take a performance test this time as I didnt believe there was anything wrong with it. I wound the engine speed up high to simulate the machine in work and no problems.
Chased up a replacement belt and fitted, run the machine for half hour, nipped the belt up again, tested, all working as far as I could tell.
Two days later I got a call to say that it had thrown a belt again. I attended, checked over the machine once again and couldnt see anything obviously wrong. Went to great effort to get a small ruler down in the guts of the machine to check if the pulley was somehow misaligned but it was spot on.
I grabbed the front of the compressor and once again can turn it freely by hand and no problem there. I removed the tensioner from the engine so I could sus out the condition of the idler bearing, no problems there, and no evidence of it being hot either.
Supplied and fitted another belt. Ran the machine at high speed, took another performance test. Readings as follows,
Ambient - 25c
RH - 95%
DP - 25c
Discharge Pressure - 1250kpa
Converted to Temp - 51c
Condensor Inlet - 52c
Reciever outlet - 38c
Suction Pressure - 200kpa
Water draining off - Yes
Vent Temp Range - 6-8c
Cycle time - Around 20 on 25 off.
I had a call today to tell me that the machine had run for about an hour today, before belt noises started and it eventually shredded another belt.
The only thing that doesn't quite resonate qith me is the suction pressure of 200kpa. I have never quite been able to get my head around the concept of the manual style control valve. If this compressor has a Red Delphi control valve with a setting of 44psi, that roughly comes to 300-ish kpa which I am significantly less than that and I have never seen a system cool properly at 300kpa.
Any opinions or feedback on anything that looks wrong from the other members here would be appreciated. I am out of ideas at the present moment. I really dont think that this is an alignment issue not considering it was fine for a month nearly two months before the problem began occuring.
I look forward to hearing from you all.
Regards,
OP.