Re: 1988 corvette, don't understand what it's doing?
Posted: Fri Jun 19, 2020 2:45 pm
Ok, so....the new condenser showed up today.
I installed the condenser, then the new accumulator and went thought the rest of the system replacing all the seals. New orifice went in as well.
When I polished the compressor (took it apart to just the cases) it lost all it's oil. Same with everything else in the system. My 88 Vette takes 8 oz from dead empty. So I put 4 oz in the compressor. I was sure to put it in through the suction port and once the system was closed I made sure to rotate the compressor about 10 times in each direction (to be sure the oil wasn't going to "hydrolock" the compressor). Then I put 2 oz in the accumulator and 1 oz in the new condenser. That takes it to around 7oz, but since I hadn't touched the evaporator, I figure the evap is holding at least one (or two) ounces of mineral oil for a total of 8 oz in the system.
Pulled it down and it held vacuum fine. Pulled it down for 45 mins to get as much moisture out as I could.
Redtek recommends to NOT fill into a "hard" vacuum. So I let it loose it's vacuum and then hit the pump again. Pulled it down to about -14, which by definition is a "soft" vacuum.
Then I hook up the redtek and put one can in. Nothing. No surprise there, it takes two to do a fill comparable to the r12 fill. Second can goes in and things start to come alive. Compressor runs, but will short cycle. High side is going very high (350 +), the low side is also going high and there is no cooling. I grab the garden hose and run it over the condenser.
Instantly, things change. Low side settles around 35 psi. High side settles in just shy of 190-ish psi. High side lines are warm, low side lines are getting condensate on them. This is all still at idle (approx 750 rpm).
Ambient is 29c (approx 84 F) here today by the car temp display. I drop a thermometer in the main vent and it drops down to 11/12c (approx 51/52 F). So, 18c drop. Not too bad. Car is getting cold inside, even with the top down.
Bumping rpm up to 1500 rpm makes it start to cycle a bit. I adjust the cut out switch and settle on just a tick below 20 psi (redtek has lower head pressures than r12). The clutch will still occasionally cycle, but only when the rpms are up.
So it appears to be good to go.
One thing I did notice is the cooling fans (has a main and an aux fan) do not come on with the AC. I'll have to re-read my FSM, but I believe the fans are supposed to come on with AC selection. It would make sense for the fan to come on as sitting at a light or in slow traffic would mean no airflow over the condenser, thus, no cooling. So checking out the wiring and relays will be the next step to see what's up with those cooling fans....
I installed the condenser, then the new accumulator and went thought the rest of the system replacing all the seals. New orifice went in as well.
When I polished the compressor (took it apart to just the cases) it lost all it's oil. Same with everything else in the system. My 88 Vette takes 8 oz from dead empty. So I put 4 oz in the compressor. I was sure to put it in through the suction port and once the system was closed I made sure to rotate the compressor about 10 times in each direction (to be sure the oil wasn't going to "hydrolock" the compressor). Then I put 2 oz in the accumulator and 1 oz in the new condenser. That takes it to around 7oz, but since I hadn't touched the evaporator, I figure the evap is holding at least one (or two) ounces of mineral oil for a total of 8 oz in the system.
Pulled it down and it held vacuum fine. Pulled it down for 45 mins to get as much moisture out as I could.
Redtek recommends to NOT fill into a "hard" vacuum. So I let it loose it's vacuum and then hit the pump again. Pulled it down to about -14, which by definition is a "soft" vacuum.
Then I hook up the redtek and put one can in. Nothing. No surprise there, it takes two to do a fill comparable to the r12 fill. Second can goes in and things start to come alive. Compressor runs, but will short cycle. High side is going very high (350 +), the low side is also going high and there is no cooling. I grab the garden hose and run it over the condenser.
Instantly, things change. Low side settles around 35 psi. High side settles in just shy of 190-ish psi. High side lines are warm, low side lines are getting condensate on them. This is all still at idle (approx 750 rpm).
Ambient is 29c (approx 84 F) here today by the car temp display. I drop a thermometer in the main vent and it drops down to 11/12c (approx 51/52 F). So, 18c drop. Not too bad. Car is getting cold inside, even with the top down.
Bumping rpm up to 1500 rpm makes it start to cycle a bit. I adjust the cut out switch and settle on just a tick below 20 psi (redtek has lower head pressures than r12). The clutch will still occasionally cycle, but only when the rpms are up.
So it appears to be good to go.
One thing I did notice is the cooling fans (has a main and an aux fan) do not come on with the AC. I'll have to re-read my FSM, but I believe the fans are supposed to come on with AC selection. It would make sense for the fan to come on as sitting at a light or in slow traffic would mean no airflow over the condenser, thus, no cooling. So checking out the wiring and relays will be the next step to see what's up with those cooling fans....