Re: Can a vacuum pump be "bad" despite pulling to proper Hg vacuum?
Posted: Fri May 01, 2020 1:20 pm
by james89dx
Tim wrote:1000 or lower microns. It would indicate a working pump in my opinion.
I gotcha, thanks. I will definitely update this hopefully by early next week with the vent temp results after the vacuum with the actual professional shop machine.
Re: Can a vacuum pump be "bad" despite pulling to proper Hg vacuum?
Posted: Fri May 01, 2020 2:47 pm
by Dougflas
Tim wrote:1000 or lower microns. It would indicate a working pump in my opinion.
It's okay to ask questions. All answers are simply suggestions by those that may have knowledge of repairing a system. Not all of us will have the same opinion all the time.
I respectfully disagree. A vacuum pump with a micron gauge on it should pull below 100; usually 50 microns.
Re: Can a vacuum pump be "bad" despite pulling to proper Hg vacuum?
Posted: Fri May 01, 2020 3:43 pm
by Tim
Dougflas wrote:Tim wrote:1000 or lower microns. It would indicate a working pump in my opinion.
I respectfully disagree. A vacuum pump with a micron gauge on it should pull below 100; usually 50 microns.
So I added a few zeros. Never matters on the debit. I hate when this happens.
Re: Can a vacuum pump be "bad" despite pulling to proper Hg vacuum?
Posted: Mon May 04, 2020 1:33 pm
by james89dx
Welp, just to update this..... zero difference after vacuum/recharge on the big boy shop equipment. He's pretty surprised too as he works on a lot of fleet Altimas and knows first hand they should be able to do into the 40's vent temps no problem.
I'm thinking this thing must have too much oil. The OE service manual calls for 2.5 oz of oil with condenser replacement (even though the entire system only holds 5.1 oz), which I did even though at the time I was thinking to myself it seems like a lot. I mean the condenser is a real thin thing too.
Pretty frustrated here as 60 degree vent temps just don't cut it in Texas.