Search found 3 matches

by Coolair
Mon May 22, 2017 2:55 pm
Forum: Automotive Air Conditioning Forum
Topic: Water Dripping from Evap, suction line warm
Replies: 3
Views: 6410

Re: Water Dripping from Evap, suction line warm

Well recovered and vacuumed then weighed in the correct amount of 134...system was no different. I think I'm going to disassemble the evaporator area to check cleanliness of evaporator and change expansion valve seems like it's starving for 134 as the low side still goes to 6 lbs when compressor tur...
by Coolair
Sat May 20, 2017 6:30 pm
Forum: Automotive Air Conditioning Forum
Topic: Water Dripping from Evap, suction line warm
Replies: 3
Views: 6410

Re: Water Dripping from Evap, suction line warm

Thanks Tim, will go with your advice. Customer had someone else look at it and replaced the binary switch for some reason I knew that wasn't the problem and they found that out after they replaced it. I told them the switch is working as it is shutting the system off when it should at 6psi.....some ...
by Coolair
Sat May 20, 2017 6:01 am
Forum: Automotive Air Conditioning Forum
Topic: Water Dripping from Evap, suction line warm
Replies: 3
Views: 6410

Water Dripping from Evap, suction line warm

So here's a mind twister.....been working on a piece of heavy equipment with a very odd situation. System when running will drip water from evaporator and will have air out vents at mid to high 40's if it stays between 60 and 70 degrees outside suction line never cold and high side lines at drier ne...